been living on a 6.5kW generator for the last three days now up here in middle New York

the generator - a Yamaha gasoline engine on a Homelite portable wheeled chassis - has been running almost nonstop for about 60 hours now, with only about 10 minutes of downtime this morning when it ran out of fuel. other than that we have been refueling it live. it was bought a year ago and prior to Tuesday it had maybe 12 hours on it since new. as far as we know, the load is well within the continuous output capacity of 6500 watts.

what i would like to know is, will it hurt or put excessive wear on anything to have this run for another 72 hours? 96 hours? should the machine be allowed an hour or few hour break? how often?

the electric utility company says its going to be at least a few days longer due to the weather getting worse as the week goes on.

When I was in the Army and we had to run off generators in the Field- It was customary for us to shut off power every 6 hours to check the oil and air filter as well as to fuel them up. (these were diesel though) ,

But you should probably read the manual... and occasionally shut it down to check the oil and air filter as well as to refuel. ( I would say every 4 - 6 hours to check the fluids then let it sit for at least 10 min ) not to mention if the belts are visible then check them. (some have chains and those you have to make sure are lubed) . Not to mention you should see if there are any lube points- though probably you are snowed in and don't have a grease gun.

If not then look online for a manual- usually they have a general maintenance section.

Also to note make sure that it is in a well ventilated area.

Though after this period of use you may want to consider getting the oil changed in the generator as soon as the weather clears.

is it a premium series or an inverter series of their generators? If your generator says it's 6500W then that is PEAK, NOT CONTINUOUS. Do not operate at a maximum power for more than 30 minutes. For continuous operations, do not exceed the rated power.

For example their E6600DE is 6600 watts peak, but 6000 continuous (which is still quite high because normally continuous is 50-60% of peak) with a running time of 7.4 hours at rated load.

Check out the current ones here: http://www.yamaha-motor.ca/products/index.php?group=G

i'm positive its 6500 continuous watts. no worries there, i know the difference between peak and continuous output. by the sound of the gen outside, we aren't even getting close to the continuous max for more than a little while at a time.

i am more worried about the engine really, but at least its cold, not hot, out there right now being the middle of winter so it won't overheat or anything. i will see about checking the oil tomorrow, something we forgot about really. as for shutting it down every few hours, its not going to happen with my family. dad dumps gas into it while its running as it is.

the manual is long hidden away and i'm not going outside to find out the model. it seems to be holding up well.

the power definitely isn't clean, the blower in the furnace is a tad quieter (and slower) and the incandescent lamp in our fridge has a noticeable flicker depending on the load. but it seems to be holding up well. it powers enough of this household to keep all 4 of us happy. energy efficient integrated florescent light bulbs (the 15w kind that screw in to replace regular 60w bulbs) are used in all other light sources and they operate just fine.

its connected to our mains box with a cable that provides two leg power (2x120 or 240 volts). we are careful as to what is running. so far its lighting, two small televisions, a 3 month old fridge, a trailer-sized oil burnig furnace from the 70s that is running about 60% of the time, cable modem and router, three laptops plugged in and powered on, a water pump hooked to an underground well, and for a short time this afternoon, my Oki LED page printer. if we kill the heat, the water heater can be run, usually for 30 minutes or so at a time we give it.same with the clothes dryer. no light dimming here, though i wish i had a P3 Kill-a-Watt handy

thanks for the replies, im going to sleep now :)

Do you really need power 24 hours a day?

Why not just run it for a few hours every once in a while to have the furnace run? I hope you don't have neighbors.. Power went out here a couple weeks ago at midnight and some ******* a door down fired up his generator at 1am and ran it all night. Needless to say that's the closest I've ever come to committing a crime (vandalization / sabotage of a generator).

Do you really need power 24 hours a day?

Why not just run it for a few hours every once in a while to have the furnace run? I hope you don't have neighbors.. Power went out here a couple weeks ago at midnight and some ******* a door down fired up his generator at 1am and ran it all night. Needless to say that's the closest I've ever come to committing a crime (vandalization / sabotage of a generator).

If you have a fridge/freezer... yes you do need power 24 hours a day.

If you have a fridge/freezer... yes you do need power 24 hours a day.

a Decent fridge and freezer should keep the cold for a considerable amount of time before they need power.

Freezers also last up to 3 days. fridges not so long but still depending on how often you open it it should last 12-24 hours.

Not sure what a gen like that can handle but whole home ones are great

http://www.amazon.com/Generac-5505-Air-Cooled-Automatic-Generator/dp/B001DZLKIW

connect right to your power and it auto switches on when the power goes out... nice to have them and they run off natural gas so no refilling

Not sure what a gen like that can handle but whole home ones are great

http://www.amazon.com/Generac-5505-Air-Cooled-Automatic-Generator/dp/B001DZLKIW

connect right to your power and it auto switches on when the power goes out... nice to have them and they run off natural gas so no refilling

dad is thinking of a 12000 watt diesel for a future upgrade, as it would be more than enough to power *everything* we normally use. natural gas would be nice, but i think he'd go for diesel because it could easily be hooked into our heating oil tank and would burn slightly cleaner for a cheaper price per gallon than standard road vehicle diesel fuel.

all else: turning off the heat for an hour makes the place pretty chilly, but the fridge temp creeps up to 50 degrees which isn't good for our food. tomorrow we plan for a two to three hour break.

and about the noise? there are at least 5 generators running on our road at any given moment, although i think we might be the only ones running one constant.

First off why do you need to run a freezer 24 hours per day? It is winter outside and you could put the stuff in a cooler and leave it outside unless of course the temperature is above freezing. Second of all that is why it is always good to have a wood burning stove in situations like that where power could be out for days. Luckily during the ice storm about 12 years ago it was only for a stretch of 8 hours that we were out but had constant loss of electricity.

Turning the heat off for an hour makes the place chilly? You probably have lousy insulation if that is the case and to save energy should put on more clothes. Sheesh talk about panzies.

When our power went out because of the wind storm in the Midwest, we ran our generator 12 at a time, and never had any issues except the noise. I used good quality fuel and Castrol oil, with some Jacobs added to the gas and oil. It worked great. We had 2 freezers, and a refrigerator, and they were fine with only 12 hours a day. The trick is to keep the freezers covered to keep the cold in. We had no power for 6 1/2 days.

We are planning to get a whole house generator, Costco has a 10k NG/PG unit (12k PG) that comes with auto 100 amp switch box (it will cover up to 150 if you upgrade), which is more then enough to power my house. It can handle most homes, and only cost $1997.99. It is a little larger then an air conditioner, but something that i plan to get, (the batteries for my UPS are getting to costly).

You don't need a fridge or freezer at a time like this, just pack your food in bins, and then bury the bins in the snow to keep it cold. I've worked with generators before, run it twelve hours on, then three hours down.

aren't your powerlines underground or something? I know a lot of snow has fallen, but really, a few days without power? There would be riots if something like that happened here, no one even has a generator over here :D

nah over here in America our power grid is old and unreliable. very newly built areas usually have utility lines underground and inner city areas of course have all wiring, fuel, and water lines buried

but not out in the woods where i live, here everything is suspended in open air on poles.

147000 customers in the dark is the power co's estimate as of last night

Not had a proper power failure here in years. When we do get a failure they last an hour or two at the most. I suppose we're lucky with underground utilities in much of the UK. I suppose it's worse out in the country with the traditional suspended lines.

I hope you get your power back soon.

This topic is now closed to further replies.
  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Posts

    • I just looked on my computer and there are settings and log files for utilities I have never even turned on!
    • O&O ShutUp10 3.1.1104 by Razvan Serea O&O ShutUp10 offers a simple yet effective way to take control of your Windows privacy. It provides access to almost 50 privacy-related tweaks, most of them hidden or not easily accessible to the average computer users. Using a very simple interface, you decide how Windows 10/11 should respect your privacy by deciding which unwanted functions should be deactivated. Using ShutUp10 you can easily disable Windows Defender, turn off telemetry, disable peer-to-peer updates, turn off Wi-Fi Sense, disable automatic Windows updates, turn off and reset Cortana and more. ShutUp10 allows you to create a System Restore point before you apply any changes, so that you can revert your system at any time if you run into problems. O&O ShutUp10 is entirely free and does not have to be installed – it can be simply run directly and immediately on your PC. And it will not install or download retrospectively unwanted or unnecessary software, like so many other programs do these days! O&O ShutUp10 Free and Premium The latest version brings O&O ShutUp10 Premium, expanding the app’s long-standing privacy controls with automatic enforcement of user-defined settings. Instead of manually rechecking options after every Windows update, users can set their preferred privacy configuration once—or apply recommended settings in a single click—and the tool continuously monitors them in the background. If Windows 10 or 11 re-enables disabled features or introduces new data collection paths, Premium restores the chosen settings automatically without user intervention. The free version remains available and fully functional for manual adjustments, offering the same core privacy controls for Windows. However, the Premium tier is aimed at users who want long-term, hands-off protection, adding automatic reapplication after updates, ongoing monitoring, and optional notifications to ensure privacy settings remain consistent over time. O&O ShutUp10 3.1.1104 changelog: Added “Show Differences” button in the overview panel “Don’t show again” option for the restore point prompt Ctrl+F keyboard shortcut for search/filter functionality Detection and linking of system-wide and user-specific setting associations Automatic search while typing PREM: Option to preserve notification counters and timestamps across application restarts PREM: Reset blocked settings button in the Settings dialog PREM: Informational message when no settings are blocked PREM: Update check can also be triggered from the menu PREM: Notification deduplication and activity log summary feature Improved L005 “Disable Windows Location Service”: Version-specific split (up to Windows 11 23H2) and new variant for Windows 11 24H2+ L001 (Disable Location): Added Night Light warning to the description in all languages Search now detects setting IDs even when ID display is disabled and offers to enable it Detection and removal of Copilot/AI desktop apps in RecallTerminator Optimized High DPI support PREM: Reset button is now only enabled when blocked items exist – setting IDs are shown in the confirmation dialog PREM: Updated tray icons with higher-resolution versions PREM: Activity Log timestamps now use localized date and time formats PREM: Tray icon status now uses OK/Warning indicators and localized tooltips PREM: Recall folder detection switched to service-based detection PREM: Copilot uninstallation now provides UI feedback and improved verification Fixed Description text was not displayed correctly for the last item and disappeared when clicking the scrollbar Crash when clicking a search result heading or the […] button PREM: Installation path is now correctly preserved during upgrades PREM: Tray icon was not reliably removed when exiting the application PREM: Main window was not displayed correctly in single-instance mode PREM: Incorrect display of the & symbol in tray icon tooltips on Windows 10 PREM: Fixed notification flooding after sleep/standby PREM: Dashboard was not refreshed after applying recommended settings during onboarding PREM: Progress bar was not reset after deleting Recall folders PREM: Fixed service startup failures PREM: Fixed incorrect drift detection when Automatic Protection was disabled PREM: Notifications now correctly count all deviating settings when protection is enabled PREM: Registration Wizard was shown after sleep/standby despite a valid license Download: O&O ShutUp10 3.1.1104 | 76.4 MB (Freeware) Download: O&O ShutUp10 32-bit | ARM64 View: O&O ShutUp10 Home Page | Screenshot Get alerted to all of our Software updates on Twitter at @NeowinSoftware
    • Fascinating...W h i t e P o w e r is now also asterisks out.  
    • In the past few days I have noticed two odd moderation activities. First, when I posted the term 'White Nationist Christian' it was asterisk's out. When I changed it to **** it was allowed! Second, in the Politics is a ###business thread I was allowed to post that the GOP is a party of p e d ophiles but I was censored  when I posted the GOP are a party of p e d ophile protectors. Wtf Neowin. Please explain.
  • Recent Achievements

    • One Month Later
      Vincian earned a badge
      One Month Later
    • First Post
      Jocimo earned a badge
      First Post
    • Week One Done
      suprememobiles48 earned a badge
      Week One Done
    • One Month Later
      Windows Guy earned a badge
      One Month Later
    • One Month Later
      Prasann earned a badge
      One Month Later
  • Popular Contributors

    1. 1
      +primortal
      547
    2. 2
      +Edouard
      163
    3. 3
      PsYcHoKiLLa
      86
    4. 4
      Steven P.
      66
    5. 5
      neufuse
      65
  • Tell a friend

    Love Neowin? Tell a friend!